That’s $58.3 Billion dollars. That’s roughly how much money we wasted in 2010 in the US according to the Department of Energy because of air leaking out of our building envelopes. If your building leaks energy, you’re paying more for energy than you need to. Clearly you’re not alone. If you’re ready to claim your share of the savings, it’s quicker and easier than you think.
This is in great contrast to my friend's experience. Her attic spaces were sprayed and the foam is actually pretty, and I was in her attic 6-7 days after it was sprayed and could hardly smell anything when I stuck my face up to the foam. And she did not have to clean up one speck of dust during or after the spraying. I got the name/number of the guy from her who managed her attic project, but between the time he did my house and the time he did her house, he was let go from the company who did her attic and hired by another company. He assured me everything would be the same, etc., etc., and I had no reason to believe anything had changed, but the sprayers who did my house later admitted they had never sprayed an attic before and I also found out that the foam used in my attic was from a different manufacturer. Neither my friend nor I had any idea this guy was with different company then, until the week after they filled my attic with off ratio foam, and my home with toxic vapors.  

Thank you, Allison. We have a split system unit (actually 5) with the heat being propane. The foam guy said that it needed ventilation, so completely sealing the attic wouldn't be a good idea. It sounds like you are saying that the systems need to be vented out of the attic or replaced with some type of closed system. But I shouldn't bother spraying if the plan is to leave the soffet vents open. Is that correct?
In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides). https://www.youtube.com/v/ggLAUsiuI_o&feature=share
One of the key differentiators between traditional insulation materials and spray foam insulation is the latter’s ability to insulate and air seal. Foam insulation provides an air barrier to wherever it is applied to help mitigate air leakage from the building. Air sealing the building envelope with sprayed-in foam insulation also helps address moisture ingress to reduce the risk of mold and mildew growth as well as the formation of ice dams in colder climate zones during the winter months.  When you compare foam insulation with traditional fiberglass insulation and cellulose insulation, sprayed insulation minimizes air infiltration, it assists in limiting moisture vapor from entering and escaping the home, which in turn reduces the load on heating and cooling systems. Below is a video that compares fiberglass, cellulose and open-cell spray foam in terms of insulating and air sealing value.
Solvent-based polyurethane coatings have excellent adhesion and when used as a base coat over asphalt, EPDM, TPO or PVC, it eliminates the need for a primer. The resulting savings on labor and material more than offsets the higher cost of the product. When top coated with silicone, it gives you the best of both worlds. It's also an excellent gutter and RV coating.
“It’s been scientifically proven that the temp of the shingles rises only a couple of degrees when there is an unvented attic compared to a vented attic,” said Garry Barlow, estimator at RetroFoam of Michigan. “If we lived in a southern state it has been proven that the longevity of the shingle did diminish by only one year. In the northern states there was no difference in the life span of the shingles.”

Spray Foam Basement Walls


Sporadic cases of hypersensitivity pneumonitis (HP) have also been reported in workers exposed to isocyanates. The symptoms may seem like the flu, with fever, muscle aches, and headaches. Other symptoms may include a dry cough, chest tightness, and difficult breathing. Individuals with chronic HP often experience progressively more difficult breathing, fatigue, and weight loss. Individuals with acute HP typically develop symptoms 4–6 hours after exposure.[4]
After researching this, Im curious about a method called poor mans sprayfoam where foamboard is cut to size between studs and sprayfoamed around the perimeter. Aside from the labour doing the job yourself, the cost seems comparable, is one better than the other? What about the quality of the canned sprayfoam around the perimeter? When i see sprayfoam done, it is never a full depth of the studs, so you would get 2.5-3 inches in a 3.5" (2x4) wall. Any thoughts?  https://m.youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o
Spray foam is a chemical product created by two materials, isocyanate and polyol resin, which react when mixed with each other and expand up to 30-60 times its liquid volume after it is sprayed in place. This expansion makes it useful as a specialty packing material which forms to the shape of the product being packaged and produces a high thermal insulating value with virtually no air infiltration.
Roof coatings made with acrylics, urethanes or asphalt soften under the stress of ponding water or snowpack. Eventually, these roof coatings will bubble and peel away from the substrate, leaving your roof vulnerable to leaks, rot, and decay. However, GacoRoof’s 100% silicone formulation is designed to stand up to whatever the elements dish out. Silicone will withstand areas of ponding water without softening, bubbling or peeling from the substrate. Acrylic, urethane and asphalt roof coatings decompose and wear away from the stress of harsh sunlight, UV rays, and freeze-thaw cycles.
I did a LOT of prep before using this product. Cleaned, vacuumed, installed additional insulation etc etc etc. This spray foam was easy to work with, and did it's job as it was supposed to. If you are curious, this kit was purchased because - every "foam insulation company" I contacted either did not call back (due to no interest) OR this was too small of a job. That is why I went DIY on this one, that and: I was advised by one of these companies that they have a minimum $2k job because ... (insert your answer here, but I will choose that everyone needs to eat).

Spray foam insulation or spray polyurethane foam (SPF) is an alternative to traditional building insulation such as fiberglass. A two-component mixture composed of isocyanate and polyol resin comes together at the tip of a gun, and forms an expanding foam that is sprayed onto roof tiles, concrete slabs, into wall cavities, or through holes drilled in into a cavity of a finished wall.
Spray foam insulation, like other insulation, saves on energy costs and lowers utility bills. Studies by the US Department of Energy show that 40% of a home's energy is lost as the result of air infiltration through walls, windows and doorways. Buildings treated with spray foam insulation insulate as much as 50% better than traditional insulation products.

Spray Foam Insulation


Silicone coatings are typically produced by adding a catalyst and solvents to a silicone base. Because the silicone is a natural material, these coatings are bio-degradable. They can be applied to a roofing system using many different techniques, including spraying or rolling. Silicone coatings are available in many colors, including reflective white and translucent.

Part of that guidance will be explaining that interior, two component foam is applied with the professional using specific personal protective equipment (high-pressure foam is installed while using a respirator, for example). It is encouraged that professionals explain clearly to customers that this equipment, coupled with certain work and engineering practices, including ventilation, is used to minimize exposures to the chemicals used to make SPF during the job.


What more is that we also think it is one of the most durable among liquid roof coatings on the market. It can last for several years, working continuously in protecting your roof from outside elements, such as dust, leaves, twigs and debris that would otherwise damage your roof. When it happens, your roof might have leaks and cause discomfort inside your RV.
The complete line of JM open- and closed-cell spray foam insulation solutions provide superior thermal and energy performance, as well as advanced air, moisture and sound control in any climate. These products can be used in interior and exterior walls, unvented and vented attics, floors, ceilings and crawl spaces. Plus, using spray foam can reduce air leaks and create a more comfortable, energy-efficient home – meaning you could see more energy savings every month.

How Much Is Spray Foam Insulation Cost


You probably have some familiarity with spray foam insulation, and you may have even used the foam that comes in pressured spray cans at home improvement retailers. This foam is know as one-part foam, meaning that it is one continuous mixture that is simply applied to the area in need. One-part foam is frequently used for sealing small gaps and cracks.
Most closed-cell spray foam is now formed using hydrofluorocarbon (HFC) blowing agents that have high global warming potential, partially or completely offsetting the climate benefits of the energy savings they can offer. In the United States, HFCs are scheduled to be phased out by January, 2021. A few spray foam suppliers have started supplying spray foam blown with hydrofluoroolefin (HFO) blowing agents without this problem as of early 2017.[14]
Heat which is created elsewhere that is transported by means of a fluid, such as water or in our case air. Spray foam insulation's most important attribute is the ability to air seal creating a custom airtight envelope within the building structure. The added benefit to air sealing is the ability to block convective heat transfer from interior to exterior during heating months and vice versa during cooling months, as the heat cannot escape through gaps in the buildings envelope without the aid of air movement from infiltration as a means of transport.

How Much Does It Cost For Spray Foam Insulation


Sean, thanks for jumping in and answering John's questions. About choosing the right foam, I intentionally avoided the open cell vs. closed cell foam debate. I did this partly because it's worthy of an article all by itself, but mainly I didn't include it because, despite all the warnings the two sides issue about the other, I've never personally seen a problem caused by using open cell where they should've used closed cell or vice versa. I'm sure things like that happen; I just haven't seen it yet.
The problem was that the installer was doing his first spray foam job ever, and the thickness of the insulation varied from zero (visible roof deck) to about 9". Unfortunately, good average thickness doesn't cut it. The coverage needs to be uniform because a lot of heat will go through the under-insulated areas. (See my article on flat or lumpy insulation performance.) https://youtube.com/watch?feature=youtu.be&v=ggLAUsiuI_o
Most flat roofs are not perfectly sloped, causing water to puddle in some areas, in particular around the drains and scuppers. Many roof coatings are not rated or warranted for "ponding water", and thus might fail pre-maturely if exposed to standing water over long periods of time. Serious consideration should be given to the performance and limitations of the coating being selected. Some manufacturers will warranty their coatings including ponding water. Typically, manufacturers for acrylic roof coatings do not include warranties for ponding water, while some polyurethane and silicone roof coatings manufacturers will.
Spray foam insulation is typically priced by volume, meaning your cost will depend on how much material you need to use to insulate your space, although other factors may influence price as well. In most cases, the cost of spray foam insulation is more than worth it, as it's a once and done upgrade that will not only provide energy savings in your home, but also improve your home's overall comfort.
While the R value will vary, most ocSPF products have an R value of around 3.8 per inch. Unlike medium-density closed-cell SPF, ocSPF is not a vapour barrier. When installed at 5.5 inches or more, ocSPF does act as an air barrier. It is often used for interior walls because it provides sound reduction by blocking and absorbing air leakage. It is usually only recommended for indoor applications.
Steve: If your spray foam installer leaves the vents open, he will be committing the 2nd of the 4 problems I described above. You will most likely have comfort and efficiency problems. You may well have condensation problems. You will be spending a lot of money on a product that likely won't perform as it should. Don't let him leave the vents open. If the installer you've chosen doesn't understand this, you may want to choose someone else. 
I had a hole in the drywall in our bathroom that was about 2 in x 5 in that I used Great Stuff to fix. I am impressed with the characteristics of the filler. It filled the hole completely in a few seconds of application. I will warn anyone using it though to make sure you don't fill the hole entirely flush to the wall because this stuff continues expanding after you apply it. I didn't think about that but no big deal really because you can sand it which is exactly what I did, and then applied spacial and paint and it is almost as good as new. For the price this was a heck of a deal because I only used a tiny amount and now am left with nearly a full can. I guess I will have to find somewhere else to use it now. Great product, ... full review
I did a LOT of prep before using this product. Cleaned, vacuumed, installed additional insulation etc etc etc. This spray foam was easy to work with, and did it's job as it was supposed to. If you are curious, this kit was purchased because - every "foam insulation company" I contacted either did not call back (due to no interest) OR this was too small of a job. That is why I went DIY on this one, that and: I was advised by one of these companies that they have a minimum $2k job because ... (insert your answer here, but I will choose that everyone needs to eat).
Spray foam insulation, when properly installed is both an air barrier and when closed cell foam is used at the proper depth a vapor barrier!  Before hiring any contractor you should establish the brand of foam being used and verify that with the named manufacture.  Please ask for ESR reports and MSDS sheets on any foam being installed in your home. A couple areas where you might consider spray foam insulation include: http://www.youtube.com/v/ggLAUsiuI_o&feature=youtube_gdata

Global warming potential (GWP), as defined by the EPA, is a measure of how much energy the emissions of 1 ton of a gas will absorb over a given period of time, relative to the emissions of 1 ton of carbon dioxide (CO2).  Spray foam insulation products that use water as the blowing agent - typically open-cell foam however Icynene’s ProSeal Eco is a 100 percent water blown closed-cell spray foam – have a global warming potential of 1, the lowest possible number.  This is because water in the mixture reacts during the application process to release carbon dioxide and heat. The GWP of the blowing agent is that of carbon dioxide. Carbon dioxide has a GWP of 1. https://youtube.com/watch?feature=youtube_gdata&v=ggLAUsiuI_o
This stuff works GREAT ! I live in an older mobile home that had a lot of leaks when I moved-in. I worked for two years to locate and fix them all. Now I simply go over all of the repaired places once a year just to be sure everything is OK. NO LEAKS FOR 4 YEARS NOW!!  Others here use "sno proof" or something that does not stop leaks. When I tell them about my success, they don't seem to want to pay the$ for this superior product. Too bad!. I used the tape in  repairing the leaks.
One of the key differentiators between traditional insulation materials and spray foam insulation is the latter’s ability to insulate and air seal. Foam insulation provides an air barrier to wherever it is applied to help mitigate air leakage from the building. Air sealing the building envelope with sprayed-in foam insulation also helps address moisture ingress to reduce the risk of mold and mildew growth as well as the formation of ice dams in colder climate zones during the winter months.  When you compare foam insulation with traditional fiberglass insulation and cellulose insulation, sprayed insulation minimizes air infiltration, it assists in limiting moisture vapor from entering and escaping the home, which in turn reduces the load on heating and cooling systems. Below is a video that compares fiberglass, cellulose and open-cell spray foam in terms of insulating and air sealing value. https://www.youtube.com/watch?v=ggLAUsiuI_o&app=mobile
DID YOU KNOW? Spray FOam insulation out-performs conventional insulation materials because they (conventional insulation materials) trap still-dry air and if that air moves or becomes wet, the thermal resistance can drop by 50%. Spray Foam protects against air infiltration, which can increase energy costs in buildings by 10 to 40%. Eliminate these drafts and live in a more energy-efficient, comfortable and healthier building by choosing spray foam insulation.
In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides).
I used this product to seal and insulate my rim joists as I am finishing the basement. The builder used R13 batt insulation when we built the house 3 years ago. I use a dehumidifier to control moisture in the basement which is below grade. The setting I use is 55%. The dehumidifier kicks on periodically and requires emptying every few days. Since using the foam all around the house on the rim joists and sill plate, the dehumidifier has stayed at 50% for over two weeks since spraying and rarely turns on anymore. I also put the original R13 batt insulation back up after the foam cured.

Spray Foam Hot Roof


Spray foam insulation systems effectively seal walls, roofs, corners and other surfaces, creating a more comfortable household because it provides a barrier against drafts and associated pollen and dust. Long-term, properly installed spray foam won’t change its form or shape, meaning it will deliver the same benefits that it did years—or even decades—after being installed, while other insulation materials may settle and create future gaps in the insulation. 
Spray foam insulation, like other insulation, saves on energy costs and lowers utility bills. Studies by the US Department of Energy show that 40% of a home's energy is lost as the result of air infiltration through walls, windows and doorways. Buildings treated with spray foam insulation insulate as much as 50% better than traditional insulation products.

Spray Foam Insulation


Acrylic coatings are typically applied in two coats, with the second running perpendicular to the first. 1 gallon per 100 square feet is a good estimate for these coatings, as they do not need to be applied nearly as thick as many other coatings. These coatings can be sprayed or roll-applied. Acrylic coatings generally require a re-coat within 2-3 years of application.

I used this for the rim-joist in our home. A couple things: I put 1in solid core foam (cut to size) in each bay before using the spray foam. I also was able to do a relatively 'thick' spray to close off any potential gaps that may have existed. I turned off the HVAC and turned on some fans in the windows to exhaust out the fumes, and wore a mask (3m respirator).
I have never used foam insulation before and this was easy for me to use right out of the box. I had a 4'x8"x8" cavity in my basement that houses a waterline. When the previous homeowner installed this they put no insulation in at all and being that it's an exterior wall in the basement and I live in the Midwest that thing was pushing so much cold air in it was incredibly uncomfortable. Out of the box and job completed in about 5 minutes. Stopped all drafts and created a nice 2" barrier on the wall in which I will install some extra bat insulation over it. 4 stars because the spray isn't very good passed 6-8" from the surface. Make sure you can reach the surface you want to coat. Great for small jobs! http://www.youtube.com/watch?v=ggLAUsiuI_o&feature=youtu.be
I am on my third project with foam it green. I like the simplicity of it, the color blending to make it green, it alerts you quickly if something is wrong with the blending so you don't waste alot of valuable material. Follow the instructions closely, put in the prep time and you will have no issues. It seems most people's negative comments have to do with not following instructions or guidelines. It is about as close to point and shoot as you can get but there are still some essential details that need attention. The only complaint I have is the fragility of the gun, last project I cracked one on accident but luckily needed two kits to finish the project so I had a back up, but I was more careful to gently lay the gun down between applications.

Spray Foam Basement Ceiling


Roof Coatings should not be confused with deck coatings. Deck coatings are traffic bearing - designed for waterproofing areas where pedestrian (and in some cases vehicular) traffic is expected. Roof coatings will only waterproof the substrates but will not withstand any kind of on going use by people or vehicles (such as walkways, patios, sundecks, restaurants, etc.). http://youtube.com/e/ggLAUsiuI_o?app=desktop
Roof coatings made with acrylics, urethanes or asphalt soften under the stress of ponding water or snowpack. Eventually, these roof coatings will bubble and peel away from the substrate, leaving your roof vulnerable to leaks, rot, and decay. However, GacoRoof’s 100% silicone formulation is designed to stand up to whatever the elements dish out. Silicone will withstand areas of ponding water without softening, bubbling or peeling from the substrate. Acrylic, urethane and asphalt roof coatings decompose and wear away from the stress of harsh sunlight, UV rays, and freeze-thaw cycles.

How Much Is Spray Foam Insulation Installation

×